Electric meter upgrade

Hello, My electric company wants to upgrade my meter to a smart meter. I have the option to opt out of the variable rates, but they change current rate measure in KVH to KVA. (KVA if I Opt-out of meter upgrade. The opt-out rate skyrockets from to 3.85 per KVA when usage exceeds 250 KVA average over a 15min period.

I must add I have many aquariums that have pumps that run 24hrs a day.

Im trying to figure out how I can configure my sense to figure out which rate will be better. And can sense measure how many KVA you are using? Thanks in advance!

A little power / energy education:

  • kVA and kW are both measures of power and are closely related. kVA is a measure Apparent Power, while kW is a measure of Real Power. I’m not going to go into a definition of each except to say 2 things - 1) the difference between the two is related to the phase angle difference between the AC voltage and AC current flowing through your house and 2) for most homes, unless you are running very large motors continuously, the phase angle is near zero so the Real and Apparent Power measured for homes should be within 5%.
  • Sense measures the Real Power in kW, so you might want to add 10% to your Sense reading to get max possible kVA, because kVA will always be equal to or larger than the kW reading.
  • The numbers from your utility really surprise me - you sound like you are an industrial customer. 3.85c / per kVA sounds very cheap (I’m guessing your unit is cents). And a 250kVA usage over 15min would be 62.5kVAh, a crazy large amount of energy. The biggest power user in my house, charging my Model S at 80A, is only about 20kVA.
2 Likes

$3.85 not 3.85 cents per kVa

Have killawatt tester, We tested a compact fluorescent bulb. It used 9w or18 kVa

Anyway I’m looking for help with sense.
I would like to set it up so that I can see what my bill would be like in both scenarios.

OK - that price makes more sense though I’m still confused about the units.

  • House kVA should run roughly 5-10% greater than kW usage, unless you have unusual loads.
  • Florescent bulbs are fairly inductive so a 9W compact bulb will have an apparent power of 14VA (NOT kVA).
  • Even if your Apparent Power kVA is 2x your Real Power (kW), it would be very hard to hit 250kVA over 15 min. That would be 125kW over 15min.
  • I’m a little thrown by units - $3.85 / per kVA is a bit meaningless because kVA is not a measure of energy. Maybe they meant kVAh ?
  • This kind or billing is what is known as a demand charge - Sense doesn’t directly support that in the cost function. But you could set an alert to let you know when you go beyond the pages where the demand charge kicks in. Or you could look back at the past year and see if you ever went above the point where you would start paying the demand charge.
2 Likes

I would agree with Kevin, home use even aquariums you shouldn’t see crazy difference. Most of your circ pumps for the aquariums, I would venture to say, are no bigger than 1/10hp each… My 1" saltwater pump was turning over the tank 7 times an hour, 180gal tank one pump and it was 1/10hp. My pool and hot tub these days are way more of a motor load than my aquariums used to be. pool is 2hp, and the hot tub has four 1.5hp motors. My home AC unit is 3-ton and with all of that stuff running, I still don’t see a crazy low power factor at my place.

1 Like

And if you’re confused by the various abbreviations, I’ll try to help. Not trying to be demeaning, but sharing what others have shared with me.

Hopefully you already understand amps and volts, but just in case…

Volts: measurement of electrical potential.
Amps: measurement of electrical current.
Power is (volts) * (amps) and is an instantaneous measurement (rate) usually expressed as watts (W) or kW (watts / 1000). It is also acceptable to just carry through the units of volts and amps (1000 watts = 1000 volt-Amps = 1 kVA).
Energy is a cumulative total of average power (W, kW or kVA) over a time interval (typically hours). So consuming electricity at a rate of 1000 W for 1 hour equals 1 kWh of energy used.

The math really is this easy if all you’re electrical appliances are “resistive” loads like water heater and electric ovens. In that case, real power and apperant power are the equal, and the ratio of them (called the power factor) is equal to 1.

As mentioned earlier, some things like motors and fluorescent lights bring some black magic into the mix. For whatever reason, they have a power factor of something less than 1. In these cases the real power (volts * amps) is only a portion of the power that the utility must provide. The rest is called reactive power and is never expressed in watts, only in volt-amps-reactive or kilovolt-amps-reactive (VAR, kVAR). Apparent power is calculated using some relationship between real and reactive power, and is (nearly?) always larger than real power (watts). This can also be calculated using a known or estimated power factor. (Real power / power factor = apparent power). Apparent power units are always VA or kVA. Utilities want to minimize the reactive power they have to supply (i don’t know why) and so they sometimes penalize larger customers (factories and such) for having low power factors. Target (overall) power factors typically range from 0.8 to 0.95. But individual devices may have power factors of 0.2 or lower. Summary: kilowatts (kW) and kilovolt-amps (kVA) are similar but not usually the same.

Demand charge is something entirely different. The utility’s perfect scenario is supplying a fixed, predictable amount of power to the grid around the clock. Any time the demand changes, they have to load/unload generation capacity, etc. They also have to ensure that they have the infrastructure to support the entire system on peak energy days. The demand charge is how they do that. It “penalizes” users with high spikes in demand by charging them for their peak usage and enables the utility to install and maintain the infrastructure necessary to provide reliable power under peak loads. A 15 minute average is a common way to calculate a demand charge. Units would typically be watts (W, kW) or volt-amps (VA, kVA).

Time of use rates are structured to discourage high consumption during periods of peak demand and encourage more use when demand is low. In this way the utility can incentivize a more stable load pattern and possibly smaller infrastructure overall. Because they WANT you to use more power when demand is low, time of use rates are typically NOT used in conjuction with demand charges (i think).

Demand charges are entirely separate from consumption charges. For your situation, you should have a demand rate AND a flat energy rate. If your demand rate really is $3.85 per kVA for anything over 250 kVA, you’ll likely never notice. For example, i have a 200A, 240V main service. That’s 48,000 volt- amps or 48 kVA. I don’t think power factor even plays a role here (someone smarter than me can feel free to weigh in on this), but let’s assume it does (worst case) and my power factor is 0.5 (REALLY LOW) at peak load. That would give 96kVA… still less than half of the point that triggers a recalculation of the demand charge.

But this is only a portion of your utility bill. The other is your consumption which should still be calculated based on a total of kWh used. That rate is entirely separate from the demand rate.

I hope this was helpful… taken WAY longer to write this (on my phone) than i thought it would!

4 Likes

This topic was automatically closed 365 days after the last reply. New replies are no longer allowed.