We had a big storm maybe a month ago and lights have been flickering in the evenings on some nights. The UPS for the PC kicks in on occasion and we also seemed to switch to the powerwall reguarly for very short period of time (99 times over a month, for a few seconds each time)…
Neighbors didn’t have any comparable issues.
A quick checkat the main breaker, something is wrong
Turns out the phase on the left is not in the connector on the breaker, it’s just resting against.
No oxy-guard either, the arcing actually vaporized the metal and deposited on the set screw (among other things) which is now fused in place on that side.
The cable on this phase is actually too short to reach inside the connector! Obviously heated, deposited aluminum on the tip.
Left connector obviously heated up significantly, the twist in the connector is my doing, trying to force it open, but the set screw is fused to the connector, had to replace the unit.
Replaced the wire and the breaker yesterday (I’m EE by trade, did electro-tech at uni) all good now, but feel like that was a close call. Assumed it was a supplier (PGE) issue for a long time…
We had solar installed 2 years ago, and powerwalls 1 year ago, so not sure who’s shaddy work caused this, and I’m surprised we were fine for so long considering the state of the setup…
We were inspoected multiple time too for each of these installs (3 times for the battery install, so I’ve got my idea of where this is coming from). Criminal negligence asfar as I’m concerned…
Glad to have it all resolved! Power quality monitoring was very helpful, and I’ll keep an eye on it to confirm everything is resolved going forward!